I came across a couple practice NEC questions and had some questions:
1) An air conditioner (compressor and fan) with a FLA of 55 Amps will be installed on the rooftop. What is the maximum rating of the short circuit protection?
A) 50A
B) 100A
C) 200A
D) 250A
Answer is B, which makes the most sense but according to sec. 440.22, the max rating should not exceed 175% of the FLA, correct? I don't see any exceptions? So if 90 and 100 were options, would 90 be the correct answer?
2) What is the maximum overload setting for a 100HP, 3ph, 460V motor?
A) 50A
B) 150A
C) 200A
D) 250A
Answer is B.
To gather overload settings, we would need to use NP value right? If that is not given, we then use the tables in article 430?
And again, the max overload setting should not exceed 115% of the FLA but 150A is the best standard value choice?
3) The continuous load in a commercial building is 645A. What is the size of the aluminum grounding electrode conductor required to effectively ground the service?
A) #1AWG
B) #1/0AWG
C) #2/0AWG
D) #3/0AWG
Answer is D.
When they say "continuos load" in this problem, does that imply the 1.25 factor has already been taken into consideration? And are they asking for grounding conductor (250.66) or equipment ground (250.122)? My assumption was grounding conductor but that wouldn't get us the right answer.
4) Determine the conduit size for a secondary feeder of a 225kVA, 480-208/120V, dry-type transformer.
How do you know to assume non-continuous load? They sized the cable for 624A (225kVA/(1.73*208)).
Thank you.
1) An air conditioner (compressor and fan) with a FLA of 55 Amps will be installed on the rooftop. What is the maximum rating of the short circuit protection?
A) 50A
B) 100A
C) 200A
D) 250A
Answer is B, which makes the most sense but according to sec. 440.22, the max rating should not exceed 175% of the FLA, correct? I don't see any exceptions? So if 90 and 100 were options, would 90 be the correct answer?
2) What is the maximum overload setting for a 100HP, 3ph, 460V motor?
A) 50A
B) 150A
C) 200A
D) 250A
Answer is B.
To gather overload settings, we would need to use NP value right? If that is not given, we then use the tables in article 430?
And again, the max overload setting should not exceed 115% of the FLA but 150A is the best standard value choice?
3) The continuous load in a commercial building is 645A. What is the size of the aluminum grounding electrode conductor required to effectively ground the service?
A) #1AWG
B) #1/0AWG
C) #2/0AWG
D) #3/0AWG
Answer is D.
When they say "continuos load" in this problem, does that imply the 1.25 factor has already been taken into consideration? And are they asking for grounding conductor (250.66) or equipment ground (250.122)? My assumption was grounding conductor but that wouldn't get us the right answer.
4) Determine the conduit size for a secondary feeder of a 225kVA, 480-208/120V, dry-type transformer.
How do you know to assume non-continuous load? They sized the cable for 624A (225kVA/(1.73*208)).
Thank you.