GrayOne...
D) is the correct answer, but the explanation is flawed! Here is the Long answer!
This problem is easily solved using the using the DIN (German) or CEI (European) Norme. Phase-displacement between a transformer’s primary and secondary windings is determined with a method called Vector Groups. A brief explanation follows:
The higher voltage winding, whether delta or wye, is expressed with capital letters, ‘D’ or ‘Y’. Correspondingly, the lower voltage winding is ‘d’ or ‘y’. The displacement or phase-shift is expressed by a number related to the hour-hand on a clock, representing multiples of 30⁰!
For example, Dy11, would mean a Delta (HV) winding, a Wye (LV) winding and the number 11 represents the 11th hr on the clock, which is 30⁰ ahead of 12:00! Thus the secondary leads the primary by 30⁰! Conversely, if the number were 1:00 or 30⁰ after 12:00, secondary lags the primary by 30⁰!
Using the above, and defining Gen voltage as the reference, line-voltage would lag or lead generator voltage by 30⁰!
Now the Short answer… line-current must always lag line-voltage by 37⁰ because that is what was “Given”!!!
Regards, Phil Corso