I'm working on a coffee shop that has a 200A 208y/120v 3 phase panel. 12 mo peak demand from utility is 83kw. Typically I default to .9 power factor. Even with that, my peak demand is over panel amperage.
Is .9 a good power factor to default to?
Is it more likely the power factor is closer to .8?
Peak demand values are peak load for minimum of 15 minutes. I'd imagine if it was 208A draw for 15 min the breaker should have tripped unless it's a faulty breaker.
Is .9 a good power factor to default to?
Is it more likely the power factor is closer to .8?
Peak demand values are peak load for minimum of 15 minutes. I'd imagine if it was 208A draw for 15 min the breaker should have tripped unless it's a faulty breaker.