No. You throw all that data away and look for another way to determine the existing load.
Riddle me this: If I told you how many miles I drove each month during 2017, can you tell me whether I was ever at risk at receiving a speeding ticket?
KWH is a measure of the total energy used - analogous to miles driven. KW is a measure of how fast you are using energy - analogous to driving speed.
In order to determine the existing load, you need to know the maximum measured KW, and KWH cannot possibly help you find that number. Ask the utility whether they can give you the peak KW for each month, and you will have what you need.
That equation will give you an answer in amps, not in KW. But if the utility information really is the peak KW for each month, and you use the highest value for the year, then this will give you a result that you can use as the existing load.KW/.8*1.25%/ 831=KW Does look better?
It doesn't explicitly say that, but I believe it means that. Look at 220.87(2). It says to take the maximum demand (without clearly saying KW or KVA) at 125%, add the new load, and check to make sure you would not exceed the ampacity of the conductors. But you can't compare load to ampacity without taking power factor into account.220.87 doesn't say you need to figure power factor or imbalance so it would just be highest kw times 1.25, done that's it.
It doesn't explicitly say that, but I believe it means that. Look at 220.87(2). It says to take the maximum demand (without clearly saying KW or KVA) at 125%, add the new load, and check to make sure you would not exceed the ampacity of the conductors. But you can't compare load to ampacity without taking power factor into account.
That equation will give you an answer in amps, not in KW. But if the utility information really is the peak KW for each month, and you use the highest value for the year, then this will give you a result that you can use as the existing load.
without starting new thread. here is my question
I have 182kw existing 600a 277480 3ph. I need to add 31.44 kw or 131 amps single phase. we are installing a single phase 480/120240 xfmr. when applying 220.87. Would i add the 31.44kw to 182kw = 213,440kw then do .8*1.25/831= 401a ? Or am I missing something.