peanut storage facility load calculation

Status
Not open for further replies.

Atm

Member
Thank you all for your help.

1. Is the approach to this load calculation correct?

2. Is 230.90 (A) Exception No 1 applied correctly?

Additional information:

service 480Y/277v four wire
480/120-240v single phase step down transformer
 

Attachments

  • rochelle load calculation.pdf
    31.2 KB · Views: 0

Atm

Member
I see that if I correctly apply 430.63 as instructed to do by 230.90 (A) Exception No 1 I would:

Add the sum of the other loads 13 amps to the rating permitted by 430.62

So 13 amps plus a 250 A device (250% times 52 FLC of largest motor is 150 amp device plus FLC of other motors in the group 108 amps is a 250 device per 430.62) yields a minimum rating of 263 amps.

If this is so and I have not made any errors, does this mean a 300 amp overcurrent protective device inverse time breaker is permitted to protect a set of 250 kcmil service entrance conductors?
 