Re: Pedestal Service
Good morning, Bob, I would take it personal if you had an issue with my point of view and you didn't take me to task with it.
There is no grey area in either situation. 250.32 permits you to use one of two methods and it is cut and dried. The problem comes with the definition of a structure and how the AHJ interprets a structure. Johndeereman has posted the definition from Article 100. Now consider a pole with a riser on it that serves a home, is that a structure that requires service equipment on it? OK, now the same pole with a meter fitting on it, is that a structure that requires service equipment on it? I believe most of us would agree that in both cases that the answer is no.
The Code is clear in stating that metering equipment is not service equipment; therefore, placing a meter in a riser does not make a service location. If I install a post, rise up on it with conduit to a meter fitting and back down to serve a home, is this now a structure to require a service?
With all that said, this argument could be taken a bit further with the addition of service equipment at the post we just installed. This is the call of the AHJ and, I believe in most cases, this will indeed be called a structure and everything downstream will fall to Article 225.
As far as 230.70 is concerned, I agree that is not grey at all. However, it is written into some local rules that a service may be inside a building for a certain number of feet. There are other areas where it is normally recognized that the AHJ "will permit" a certain distance and the electricians may use that distance to their advantage. If it is in writing and in the local amendments, I have no problem with any distance other than it is dangerous. If it is not in the amendments, I would not violate that section.