Hello Im looking for a bit of clarification. I have been back and forth with my employer on the use of 4sq boxes being used for pendant drops and its legallity.
For a visual of the installation im talking about, picture a 4sq box on the ceiling with an S.O. cord coming out to a kellems hanger, then dropping down to a 4sq box with a kellems cord connector at the bottom and a raised double duplex receptacle cover.
It has come to my attention that 4sq boxes are not technically legal for pendant drops because of the support hub rule or more so that the KOs arent rated for that use and the potential for a KO to get pushed in and hit a live terminal on the receptacle when hanging as a pendant. This we both agree on. However he says that if you were to fix (screw/secure) the 4sq to the workbench it serves, then it is no longer staining on the KOs and is legal.
My issue is that i believe securing the 4sq to a workbench or stucture violates 400.12(4) and wouldnt be a legal installation.
My only other solution to keep a legal installation would be to swap out all the 4sq boxes to Woodhead 3000 boxes so that the entire installation is "listed and labelled" for the correct use.
If you have any insight it would be appreciated.
For a visual of the installation im talking about, picture a 4sq box on the ceiling with an S.O. cord coming out to a kellems hanger, then dropping down to a 4sq box with a kellems cord connector at the bottom and a raised double duplex receptacle cover.
It has come to my attention that 4sq boxes are not technically legal for pendant drops because of the support hub rule or more so that the KOs arent rated for that use and the potential for a KO to get pushed in and hit a live terminal on the receptacle when hanging as a pendant. This we both agree on. However he says that if you were to fix (screw/secure) the 4sq to the workbench it serves, then it is no longer staining on the KOs and is legal.
My issue is that i believe securing the 4sq to a workbench or stucture violates 400.12(4) and wouldnt be a legal installation.
My only other solution to keep a legal installation would be to swap out all the 4sq boxes to Woodhead 3000 boxes so that the entire installation is "listed and labelled" for the correct use.
If you have any insight it would be appreciated.