210.52 (5) Exception to (5)
I inspected an installation that had receptacles below a countertop. The countertop exceeded 6" (bar type)and the receptacles are more than 12" below the countertop. There is a receptacle that does comply at the end of the peninsular.
I contacted the DCA and was told as long as (1) receptacle complies then the other receptacles are acceptable.
May you put receptacles under a countertop that extends more than 6"?
I inspected an installation that had receptacles below a countertop. The countertop exceeded 6" (bar type)and the receptacles are more than 12" below the countertop. There is a receptacle that does comply at the end of the peninsular.
I contacted the DCA and was told as long as (1) receptacle complies then the other receptacles are acceptable.
May you put receptacles under a countertop that extends more than 6"?