Sparky2791
Senior Member
- Location
- Northeast, PA
- Occupation
- Professional Lottery Player
Good Evening.
I am seeking an opinion on 2017 NEC 210.52 (C) (3) . Having a disagreement with a colleague on this.
My colleague says a receptacle is required on the end of the peninsular countertop in the attached drawing. I say according to the code section cited the one receptacle shown on the drawing is all that is needed.
I agree with him if this were reviewed under the 2020 NEC an outlet would be required at the end to comply with both (a) & (b) of 210.52(C)(2). But 2017 does not include that language. Was added new for 2020.
See attached pdf of drawing and picture for reference. If I am wrong would like to know what Code section is requiring the receptacle installed to the waterfall end of the countertop.
Thanks for the replies.
I am seeking an opinion on 2017 NEC 210.52 (C) (3) . Having a disagreement with a colleague on this.
My colleague says a receptacle is required on the end of the peninsular countertop in the attached drawing. I say according to the code section cited the one receptacle shown on the drawing is all that is needed.
I agree with him if this were reviewed under the 2020 NEC an outlet would be required at the end to comply with both (a) & (b) of 210.52(C)(2). But 2017 does not include that language. Was added new for 2020.
See attached pdf of drawing and picture for reference. If I am wrong would like to know what Code section is requiring the receptacle installed to the waterfall end of the countertop.
Thanks for the replies.