I came across this previous thread (now closed for replies) and would like to continue the discussion,
I am having the same problem with my Pentair IntelliFlo3 VSF pump, which is a new model just recently introduced on the market. It trips the SquareD Q0 GFI breaker intermittently once every few weeks.
Reading through all the prior comments, apparently the cause is RF noise introduced on the AC wires. Pentair's recommended solution is to use their Pentair GFI breaker which is identical to, basically a relabeled Siemens breaker. The Siemens breaker has better RF filtering to avoid nuisance trips.
Not wanting to tear out my beautiful Square D Q0 subpanel to replace it with a lesser Siemens panel, I placed a ferrite clamp on the wires leading to the pump.
Many people talk about trying out ferrite clamps and rings, but no one follows up on the thread to say if this very simple band-aid actually works.
So I would like to ask, has anyone tried a ferrite clamp/ring for this issue and what were your long-term results?
I will report back my own results but it will take a few months to confirm.
Pentair Pool Pump GFCI trips
Pentair Pool Pump GFCI trips I just completed a install of a 230V pentair vs pump and this thread had me seriously worried I'd be tripping the GFI. I ended up having to install a boost transformer to get from 208v to 232v. Could this have anything to do with why the QO gfi installed has...
forums.mikeholt.com
I am having the same problem with my Pentair IntelliFlo3 VSF pump, which is a new model just recently introduced on the market. It trips the SquareD Q0 GFI breaker intermittently once every few weeks.
Reading through all the prior comments, apparently the cause is RF noise introduced on the AC wires. Pentair's recommended solution is to use their Pentair GFI breaker which is identical to, basically a relabeled Siemens breaker. The Siemens breaker has better RF filtering to avoid nuisance trips.
Not wanting to tear out my beautiful Square D Q0 subpanel to replace it with a lesser Siemens panel, I placed a ferrite clamp on the wires leading to the pump.
Many people talk about trying out ferrite clamps and rings, but no one follows up on the thread to say if this very simple band-aid actually works.
So I would like to ask, has anyone tried a ferrite clamp/ring for this issue and what were your long-term results?
I will report back my own results but it will take a few months to confirm.