Gents,
I attached a one-line diagram that I'm looking at. It's from GE's white paper on short circuit calculations.
The 2nd attachment shows how they derive the per unit X and R values at each piece of equipment (transformers, motors, the cables, and the utility). The base power value throughout is 15000 kVA.
My questions are how they derived the X and R values where I highlighted in blue in the 2nd attachment.
For the utility (top blue rectangle): the equation to solve for the per unit impedance (Z)... shouldn't it be actual power / base power? The equation that they are using seems to be base power / actual power. The utility power is 1500 MVA. Base power as I mentioned above is 15000 KVA.
For Motor M1 (the bottom blue rectangle): what equation are they using to solve for the motor impedance X? The equation includes an X"d of 15% (sub-transient reactance) and a horsepower of 4000. I'm not familiar with the equation though. What equation is this?
Thanks!
I attached a one-line diagram that I'm looking at. It's from GE's white paper on short circuit calculations.
The 2nd attachment shows how they derive the per unit X and R values at each piece of equipment (transformers, motors, the cables, and the utility). The base power value throughout is 15000 kVA.
My questions are how they derived the X and R values where I highlighted in blue in the 2nd attachment.
For the utility (top blue rectangle): the equation to solve for the per unit impedance (Z)... shouldn't it be actual power / base power? The equation that they are using seems to be base power / actual power. The utility power is 1500 MVA. Base power as I mentioned above is 15000 KVA.
For Motor M1 (the bottom blue rectangle): what equation are they using to solve for the motor impedance X? The equation includes an X"d of 15% (sub-transient reactance) and a horsepower of 4000. I'm not familiar with the equation though. What equation is this?
Thanks!