Performing Load Assessments

Status
Not open for further replies.
Hello everyone
I'm looking for all the information I can regarding performing proper load assessments to include what size generator would be needed to provide backup power say during a power outage. For example such things as lift stations that pump sewage and also small office buildings.
 
Some helpful resources:

1) As-Built Drawings.
2) Have an electrician hook a recorder up to the main gear to get a "real world" view of demand.
3) Nameplate ratings.
 
I use Peak Demand x 125% (consider starting current). Also, If you have large VFD(s) for your "sewage" equipment you may have a low PF for your pump, which brings further design issues.
 
adavey said:
I use Peak Demand x 125% (consider starting current). Also, If you have large VFD(s) for your "sewage" equipment you may have a low PF for your pump, which brings further design issues.

That method might not work if you are using utility peak demand readings from the electric bill. In our area, that is a 30 minute average of demand. If you draw 200 kw for 15 minutes and 0 kw for the next 15 minutes, you could establish a 100 kw reading over that 30 minute period. Different utilities do it differently, but use their readings cautiously.

Jim T
 
Status
Not open for further replies.
Top