Peripheral equipment defined

Status
Not open for further replies.

Fordean

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
I read somewhere Way back That any specific equipment Whether 1/2 amp Is suppose to be dedicated wiring What is considered peripheral
I have undercounter blower water type heater in the kick plate under counter Probably 1 amp Im considering a dedicated circuit But seems a waste in circuit with only utilizing 1.5 amps of a 15 or even 20 amp capable circuit
 
The rule is not 1/2 amp. It is 1/2 of the circuit ampacity. So fixed in place equipment would only require an individual branch circuit if it was rated more than 7.5A on a 15 or 10 on a 20A branch circuit.
 
hmmmm. This is new to me. What code article describes this?

...fixed in place equipment would only require an individual branch circuit if it was rated more than 7.5A on a 15 or 10 on a 20A branch circuit....

thanks!
 
hmmmm. This is new to me. What code article describes this?

...fixed in place equipment would only require an individual branch circuit if it was rated more than 7.5A on a 15 or 10 on a 20A branch circuit....

thanks!

I was thinking of 210.23(A)(2) which says equipment fastened in place cannot exceed 50% of the branch circuit rating if the circuit contains other outlets.

It does imply that the circuit supplying equipment fastened in place with a rating over 50% of the circuit ampacity can not have other outlets.

It does not require an individual branch circuit per se, but if over 50%, all equipment must be fastened in place. No other receptacle outlets.
 
Last edited: