- New Jersey
- Journeyman Electrician
Was having a discussion with some co-workers last week regarding a receptacle installed for a permanently installed pool pump. Why is the receptacle required to be of the single and locking type if it's between 6'-10' of the pool? My guess was that so that it can only be used for the pool pump and nothing else but if you move it out past 10' then the single/locking requirement disappears. Doesn't seem to make much sense.
680.22 Area Lighting, Receptacles, and Equipment.
(A) Receptacles.
(1) Circulation and Sanitation System, Location. Recep-
tacles that provide power for water-pump motors or for
other loads directly related to the circulation and sanitation
system shall be located at least 3.0 m (10 ft) from the inside
walls of the pool, or not less than 1.83 m (6 ft) from the
inside walls of the pool if they meet all of the following
conditions:
(1) Consist of single receptacles
(2) Employ a locking configuration
(3) Are of the grounding type
(4) Have GFCI protection
(2) Other Receptacles, Location. Other receptacles shall be
not less than 1.83 m (6 ft) from the inside walls of a pool.
(3) Dwelling Unit(s). Where a permanently installed pool
is installed at a dwelling unit(s), no fewer than one 125-
volt, 15- or 20-ampere receptacle on a general-purpose
branch circuit shall be located not less than 1.83 m (6 ft)
from, and not more than 6.0 m (20 ft) from, the inside wall
of the pool. This receptacle shall be located not more than
2.0 m (6 ft 6 in.) above the floor, platform, or grade level
serving the pool.