For a permanent generator, with a dedicated 200-amp main breaker and separate load center in the basement, is there any minimum number of conduit runs needed to the generator?
I'm just curious on this because a client has a generator - supposedly the original installer only had a single conduit (underground) to the unit, but that was ripped out and replaced with 2 separate conduits (the generator is 30 KW Kohler). The reasoning was that the cables were supplying power in opposite directions and that these could not be in the same conduit.
The logic makes sense - I'm just trying to learn something for future reference - I very rarely come across a generator in residential use.
I'm just curious on this because a client has a generator - supposedly the original installer only had a single conduit (underground) to the unit, but that was ripped out and replaced with 2 separate conduits (the generator is 30 KW Kohler). The reasoning was that the cables were supplying power in opposite directions and that these could not be in the same conduit.
The logic makes sense - I'm just trying to learn something for future reference - I very rarely come across a generator in residential use.