Permanent PVC Conduit Shrinkage

Status
Not open for further replies.

mc5w

Senior Member
I want to know if anybody has encountered this problem too. The problem that I have with other people's PVC conduit installations ( but not my own ) that are exposed to cold temperatures is that the PVC conduit detaches from box connectors and LBs and then permanenly shrinks 1 to 6 inches depending on the length of the conduit run and how cold the environment gets.

To make things worse, some of these broken conduit runs are shorter than the length at which NEC requires and expansion joint.

In outdoor installations only 1 end of the PVC conduit deteaches from the box connector or LB but in blast freezers both ends of even a short run of PVC conduit detaches from the box connectors.

I am thinking of several causes of this:

1. The extrusion process for the pipe somehow creates a memory effect that operates at cold temperatures rather than heat shrinking. Some of these conduits do not have the sun beating on them long enough to create heat shrinkage.

2. I am suspicious that the diameter of the conduit shrinks faster than the diameter of injection molded parts such as box connectors and LBs.

3. The grey PVC cement that is alleged to be optimal for electrical pipe somehow creates weak joints that pull apart easily after a few years. Even a small bump from a pedestrian can break a joint.

4. I have always used clear of purple primer plus all weather ( cold temperature ) solvent cement using the same technique as for pressurized water pipes. I have not had a joint break even though some of my installations were theoretically just a little longer than the length at which NEC requires an expansion joint an I did not install an expansion joint at the time because back in 1993 NEC did not have a criteria as to when an expansion joint was required. That my joints going back to 1987 have not broken and about 10 year old work by others that is broken points to some kind of workmanship problem or maybe a change in manufacturing parameters.

One reason why I always use all weather solvent cement is that most of my customers do not think about outdoor lighting until Daylight Savings Time expires. Even if a business owner is a genius, he closes his store at 6 p.m. and then hits the sack before sunset during the summer. There is also the issue of cash flow such that outdoor electrical work gets deferred until the cold half of the year. Yes, I have tied an electric heater to one of the rungs of the ladder to keep my hands warm. I have had only about 1 instance where a major lighting project was done during the springtime.

5. Come to think of it, I have to buy primer from a plumbing supply house or from the plumbing section of a combined electrical and plumbing supplier. What I have been told by strictly electrical supply houses is that they do not carry primer because other electricians do not use it.

6. In some dirty industrial situations, dirt would tend to jam expansion couplings even if one were installed.

7. Some electricians tighten conduit fasteners so tight that an expansion coupling would not work if installed.

8. In some industrial situations, dirt would tend to contaminate primer and solvent cement.

What is your take on this?

Mike Cole
 
mc5w said:
The problem that I have with other people's PVC conduit installations ( but not my own )

LOL
icon10.gif




mc5w said:
What is your take on this?

Install the RNC to code minimum or better.

IMO if you follow the NEC rules regarding expansion fittings you will be all set.

Or Install metal raceway.

By the way using plumbers cement and primer may well be a violation of 352.48, that would be up to your AHJ.
 
PVC Conduit Shrinkage

PVC Conduit Shrinkage

None of the PVC cement on the market is UL listed. The grey cement that is supposed to be for use with electrical pipe is not UL listed. All of the PVC cement on the market is National Sanitation Foundation listed. If the cement is strong enough for pressure pipe with 50 to 80 psi water in it, it has to be strong enough for electrical purposes.

The problem is not with expansion joints or lack of expansion joints. The problem is that the grey PVC cement stops acting as cement after a few years allowing the joints to break.

Interestingly, the couplings that are swaged into the one end of the PVC pipe never detach from another piece of pipe unless installed in a blast freezer. The detachments occur with the injection molded fittings.

As I stated above, some electricians do not know that PVC conduit supports MUST be deliberately slightly loose so that expansion couplings can work. If the conduit hangers and clips are too tight, how is the expansion couplings going to work? Also, some people in building trades are incredibly strong and do not know their own strength. That is why the U.S. Navy requires that torpedoes be assembled using torque imiting wrenches and screwdrivers for all of the fasteners.
 
PVC Conduit Shrinkage

PVC Conduit Shrinkage

This permanent shrinkage and breaking of joints happens even with conduit lengths as short as a few feet in the case of a blast freezer.

The conduit never fully reexpands after joint breakage during the summer or when a blast freezer is shut down and heated up. There has to be a lie somewhere in NEC and/or the UL standard such that there is no accounting for permanent shrinkage.

I am also pretty sure that NOT using primer also violates the UL listing of rigid PVC conduit. I know the in the case of flexible ENT primer must NOT be used but that is the only case where it is not legitimate to not use primer.

Mike Cole
 
My experience with RNC is that the best way to avoid expansion problems is to:

1. Avoid long straight runs between attachment points such as boxes and secured points wherever possible. A right angle with some length beyond (say 50 diameters) will accommodate a lot of expansion.

2. Recognize the difference between support and secure when dealing with conduit between boxes. Support lets the conduit expand and contract. Secure prevents motion and prevents load on the box to which the conduit is attached. Conduit should be secured adjacent to boxes, and supported only on long runs where you need to allow expansion.

The joint in RNC, when done to instructions on the can of cement, will never be as strong as a plumbing joint. My recollection is that the instruction says to put the cement on the male part only. If you use cleaner solvent, or if you put cement on the female part of the joint, you will get solvent inside where it can attack the PVC insulation of some conductors.
 
PVC Conduit Shrinkage

PVC Conduit Shrinkage

Is a broken joint a Code violation? Heck yes.

National Electrical Code and UL do not address permanent shrinkage of rigid PVC conduit.

What I do is to let the conduit joints dry out for a few days with all of the boxes open. This dries up any solvent cement that is inside of the pipe. If the pipe is say 2 or 2.5 inches primer and solvent cement inside of the socket is essentially mandantory. Besides, I have to have an inspection for trench depth and that can be the time spent on letting the solvent cement dry up.

The cash flow of some customers is such that speed is not of the essence as it may take them 1 to 3 weeks to afford light fixtures to put up blah blah blah. That is plenty of time for the cement to dry.

Even if you put PVC cement on the male part of the joint only, you will still get some amount of solvent cement inside of the pipe.

I also suspect that some people are pulling in wires a few hours or even minutes after assembly and that weakens green joints. I have something against speed for the sake of speed because I am the one who has to fix bad workmanship by the lowest bidder. Some building owners figure out that they were expletived and then they get somebody to fix it right.

I one time made a small amount money coming in right after job "completion" to put in finishing touches that construction electricians and carpenters did not have the patience and brain cells to do. In 1 elementary school I put in a second set of light switches at kindergarten/1st grade height and then opened up the wall and lowered a drainpipe so that I could make the sink vanity small child height. The kids loved it.

This past spring I had to rewire some work I did back in 1993 and the THWN wires were not damaged by solvent cement. One reason for rewiring was that the power relay for an outdoor switched outlet had to be relocated from upstream of the GFCI outlet to downstream of the rooftop GFCI outlet because sustained power off will cause a modern GFCI outlet to trip on possible open neutral failure. The other reason was that some lampholders had to be changed to accept compact fluorescent refit floodlight bulbs that are outdoor rated. That technology did not exist in 1993.

Mike Cole
 
"What I have been told by strictly electrical supply houses is that they do not carry primer because other electricians do not use it."
Plumbing pipe and conduit are a bit different. Plus primer is not required to be used by the conduit manufacturers instructions.
1. Plumbing pipe has a hard finish, the primer softens this so the glue will adher.
2. Plumbing fittings have a slight taper, the hydraulic pressure from the taper tends to push the pipe out of the fitting.

Conduit does not have to be water tight, its just a chase.
Have you considered using fiberglass conduit? Much stronger than PVC and the joints are epoxye. Plus it does not get brittle in the cold...
 
PVC Conduit Shrinkage

PVC Conduit Shrinkage

Fiberglass conduit is not generally available around here as it is an "exotic" product. I would have to deal with an Internet w#@re#@use to get it.

Actually, I am starting to become partial to aluminum rigid conduit partly because PVC expansion couplings are like $20 each in 1/2 inch. The problem is that I cannot use aluminum conduit underground.

Some people in the oil and gas industry have told me that PVC coated steel conduit in a brine processing facility rusts anyways.

As far as PVC conduit is concerned, I would rather stick with the technique that has proven to produce RELIABLE joints.

Mike Cole
 
mc5w said:
Actually, I am starting to become partial to aluminum rigid conduit partly because PVC expansion couplings are like $20 each in 1/2 inch.

What kind of fitting are you buying?

Are they really that much?

I doubt we pay $20 for a 2"
 
I'm not an electrician, so my field experience is limited. But my guess is that if a conduit run is going to shrink by a matter of inches, there is no glue that is strong enough to hold the fittings on (assuming the fittings are solidly fastened) or to hold the couplings together.

So I'm not convinced plumbers primer keeps your conduits together while everyone elses falls apart. I am sure there are other differences that have more effect on how the conduits hold together. Like how the conduit or fittings are supported or secured, temp. differences the conduits are subjected to, ect., ect. ect.
 
I am very curious why you feel that the observed reduction in length is permanent in nature? If the conduit was installed on a hot day, and you observed it on a colder day, wouldn't the observed length necessarily be shorter? Of the PVC joints that I have observed in the field that have pulled apart, easily 50% of them were never fully seated in the fitting socket during the original install (as evidenced by the length of glue residue on the conduit ends)
 