M mark.james New User Location Salt Lake City, UT, USA Nov 14, 2013 #1 Does the NEC specify that #6 wire or smaller must be colored not just identified at each end? If so where in the code is that found?
Does the NEC specify that #6 wire or smaller must be colored not just identified at each end? If so where in the code is that found?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Nov 14, 2013 #2 It does for grounded conductors and for equipment grounding conductors. 200.6 and 250.119
B brother Senior Member Location "I have learned, in whatsoever STATE I am, therewi Nov 15, 2013 #3 don_resqcapt19 said: It does for grounded conductors and for equipment grounding conductors. 200.6 and 250.119 Click to expand... There are exceptions. see 2014 NEC 200.7(C). If the is part of a cable assembly etc... then you can identify it with tape at the terminations.
don_resqcapt19 said: It does for grounded conductors and for equipment grounding conductors. 200.6 and 250.119 Click to expand... There are exceptions. see 2014 NEC 200.7(C). If the is part of a cable assembly etc... then you can identify it with tape at the terminations.