First, I would like to thank all who contribute to this thread.
I am a code inspector. I want to know what you think about whether NM cables are permitted to be installed in a Type V (wood structure) commercial building in according to NEC 334.10 (3)
Taken from the NEC
334.10 Uses Permitted. Type NM, NMC, and NMS cables shall be permitted to be used in the following:
(3) Other structures permitted to be of type III, IV, and V construction except as prohibited in 334.12. Cables shall be concealed within walls, floor, or ceilings that provide a thermal barrier of material that has at least a 15-minute finish rating as identified in listings of fire-rated assemblies.
To me, this is very clear-cut. There is no other way to interpret this any other way. NM cables are permitted to be installed in a Type V commercial building (for example), only if it is concealed in a stud/ceiling space (or any other space) with min 1/2" sheetrock or other finish material with equivalent 15-minute fire rating. If NM cables are installed in accessible attic space, then this is clearly a violation of conditional use as permitted by NEC 334.10 (3).
Please respond with your opinions regarding this section. I have a hard time convincing someone who would not allow a can light fixture to be installed above an hydrotub, but think I need common sense in applying this section. :-?
Thanks for your input.
Mike
I am a code inspector. I want to know what you think about whether NM cables are permitted to be installed in a Type V (wood structure) commercial building in according to NEC 334.10 (3)
Taken from the NEC
334.10 Uses Permitted. Type NM, NMC, and NMS cables shall be permitted to be used in the following:
(3) Other structures permitted to be of type III, IV, and V construction except as prohibited in 334.12. Cables shall be concealed within walls, floor, or ceilings that provide a thermal barrier of material that has at least a 15-minute finish rating as identified in listings of fire-rated assemblies.
To me, this is very clear-cut. There is no other way to interpret this any other way. NM cables are permitted to be installed in a Type V commercial building (for example), only if it is concealed in a stud/ceiling space (or any other space) with min 1/2" sheetrock or other finish material with equivalent 15-minute fire rating. If NM cables are installed in accessible attic space, then this is clearly a violation of conditional use as permitted by NEC 334.10 (3).
Please respond with your opinions regarding this section. I have a hard time convincing someone who would not allow a can light fixture to be installed above an hydrotub, but think I need common sense in applying this section. :-?
Thanks for your input.
Mike