aelectricalman
Senior Member
- Location
- KY
So, a customer has an existing 1500kVAR fixed bank.
The utility company here in my state does not bill the customer for leading power factor. In the utility's eyes they look at 99% leading the same as they do 99% lagging. The only thing is they don't like it (because it affects their load planning) but they do not penalize you any different for having it.
Also, the utility demand structure is on the basis of coincident PF at peak demand.
With this being said, I have a customer that says, " I don't like the fact that on the weekends, my power factor leads at 45%". Note that they are lightly loaded. Since the utility is not billing them for this and it is not affecting his voltage adversely ( enough to trip drives), I don't see the harm. Its been this way for 10 years with no problems or drive failure.
Enter a new maintenance engineer..... He says, This is not going to work any longer. He wants to know what he can save by closely monitoring his PF and keeping it near or at unity. I told him there is little or no benefit unless he wanted to keep track of carbon emission.
Does anyone see another way this customer could save by turning off the banks on the weekend? Am I missing something?
Before you answer with the answer I think you will, consider that when the customer operates on the weekend they are at 1/10th of their normal load, therefore the PF @ 45% leading does nothing for the billing of demand. It's the PF at peak load that matters (for the utility). Peak PF always occurs during the week under load.
The utility company here in my state does not bill the customer for leading power factor. In the utility's eyes they look at 99% leading the same as they do 99% lagging. The only thing is they don't like it (because it affects their load planning) but they do not penalize you any different for having it.
Also, the utility demand structure is on the basis of coincident PF at peak demand.
With this being said, I have a customer that says, " I don't like the fact that on the weekends, my power factor leads at 45%". Note that they are lightly loaded. Since the utility is not billing them for this and it is not affecting his voltage adversely ( enough to trip drives), I don't see the harm. Its been this way for 10 years with no problems or drive failure.
Enter a new maintenance engineer..... He says, This is not going to work any longer. He wants to know what he can save by closely monitoring his PF and keeping it near or at unity. I told him there is little or no benefit unless he wanted to keep track of carbon emission.
Does anyone see another way this customer could save by turning off the banks on the weekend? Am I missing something?
Before you answer with the answer I think you will, consider that when the customer operates on the weekend they are at 1/10th of their normal load, therefore the PF @ 45% leading does nothing for the billing of demand. It's the PF at peak load that matters (for the utility). Peak PF always occurs during the week under load.