PFC & Small load

Status
Not open for further replies.
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Started a 50 HP 480v motor that had very little load on it today. It is a hammermill and had no product in it. Amps before PFC was 21, with 4. FLA on label is close to 58. I can't say that I have ever had that much change but I don't remember ever checking a motor with no load. A similar motor connected to a fully loaded fan was .84 of FLA.

Sound typical? Correction is somewhat bigger than needed for the individual motor.
 
Pfc

Pfc

Sounds about right. An idling motor consumes few watts but a lot of VARs (magnetizing current.) The PFC supplies VARs. That means the only thing on the branch circuit would be watts and those VARs not provided by the PFC.
 