POCO to the South of me has just started implementing customer owned PFC for motors 20 HP and above. I've done it for years in my immediate area. Each motor got its own PFC.
One of the issues coming up is that each irrigation system may have a well motor that has been running into SFA for years. The nameplate total of two motors on location may say 30 & 15, the POCO metering says 56 total connected. (grabbed #s form the air but they are not unreasonable) POCO is suggesting one unit total, with a FPN that few read, is that it shall not exceed the recommended KVAR for the motor. Installation would be a 20 kvar connected to the 30HP Pump Panel. Fine for a total 56 HP connection but too much for the 30 alone. Typical PFC for a 30 would be between 10 & 17.5 KVAR.
What grief, if any, will this arrangement cause?
POCO engineering had not thought of the reduced motor current seen by the overloads. Typical connection would be at the load side lugs of the starter.
One of the issues coming up is that each irrigation system may have a well motor that has been running into SFA for years. The nameplate total of two motors on location may say 30 & 15, the POCO metering says 56 total connected. (grabbed #s form the air but they are not unreasonable) POCO is suggesting one unit total, with a FPN that few read, is that it shall not exceed the recommended KVAR for the motor. Installation would be a 20 kvar connected to the 30HP Pump Panel. Fine for a total 56 HP connection but too much for the 30 alone. Typical PFC for a 30 would be between 10 & 17.5 KVAR.
What grief, if any, will this arrangement cause?
POCO engineering had not thought of the reduced motor current seen by the overloads. Typical connection would be at the load side lugs of the starter.