We installed a 3ph transformer 480v to 208.
this runs from a 480 bus to the transformer to a 208 breaker panel.
With the main on the panel off we measure 108v ( wire to ground) and 207 across legs all 3 good.
With the main breaker on we measure the same.
turn on any breaker and the voltage measured leg to ground measures 158 - 198v, except 1 leg measures 14.6v
across the legs and I get 207v.
no netural installed..
got no ideal I'v been over this ane over this.