on 480 3 Phase color code is Brown Orange Yellow
on 120/240 3 phase it is Black Red Blue I think
so what is it on 120/208 3 phase

and the hi leg was mark Red I would like to know and where to find this

thank you Bud Bell
 
Last edited:

raider1

Senior Member
Staff member
Location
Logan, Utah
Welcome to the forum.:)

There is no NEC established color code for 3 phase systems.

Brown, orange, yellow is an industry standard practice for 480/277 volt wye systems

Black, red, blue is an industry standard practice for 208/120 volt wye systems.

Black, orange (High leg), blue is an industry standard practice for 240/120 volt 4 wire delta systems.

The high leg of a delta 240/120 volt system is require to be phased Orange when the identification of the high leg is going to be done with phase tape.

Take a look at 110.15.

Chris
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
also, if you have two (or more) voltage systems in the same premises, you might want to look at 200.5 and 210.5
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Technically speaking, the orange high-leg requirement does not apply at accessible points where the neutral is not present.
 