drcampbell
- The Motor City, Michigan USA
- Registered Professional Engineer
Read the label, and you'll see "12 poles maximum". So you can install 4 full-size 1" breakers and eight half-size ½" breakers.
It's 6 full size and 12-1/2 size. There are already 4 full size on the right and it will accept 2 more on the left. Each full size slot will accept 2-1/2 size CB's.
This panel cannot accept 12 1/2-size breakers as the bottom two busbars are not made for them. It can only accept 8. 8 half-size, plus 4 full-size, makes 12 poles total. This is what is printed on the panel cover.
Not sure where your photo came from but it wrong.
Well, I guess the OP's photo is wrong then.
Not this time. Would have been nice... Typically there is an adhesive label across the two breaker knockouts stating "Do not remove."
I don't think they're metal. House mice? Ordinary residential basement debris? The house is probably 50-70 years old.What's with the metal shavings between the incoming lugs?
Didn't notice that. Thanks for the keen eye.It the insulation of one of the feeder conductors squished under the screw?
That loadcenter is not that old, if it were it wouldn't have the all plastic assembly that the bus bars are attached to. Panel was probably made no earlier then about mid 1980's, but guessing maybe even more like into 1990's when they switched to the all plastic interior body. More familiar with Square D on this kind of thing, but I think most everyone started to do that about the same time to remain competitive.I don't think they're metal. House mice? Ordinary residential basement debris? The house is probably 50-70 years old.
So I could be slightly older then I first thought, 50-70 years puts you into 1947-1967 being the install date, don't think there were plastic interiors yet in those years. The THQ breaker line that still exists today probably wasn't even developed yet in 1947, most product lines still in use today were not around before about 1955-1960 I think.I think I-T-E Imperial & later Gould/I-T-E in the 1970's was the first w/ the plastic interiors, later SQ D copied it, then GE, Siemens continued it after buying I-T-E, & converted Murray (Crouse-Hinds) also, Eaton/ C-H, still uses steel interiors for both the BR & CH lines.