Phantom/ghost voltage
Joey94
Illinois
Apprentice
Why my klein tools cl390 clamp meter measures ghost voltage while my digital multi meter won’t?
First picture the DMM shows 0V
Second with CL900 on LoZ setting no Voltage
Third picture show 17V
The LoZ setting should be your clue. A high-impedance meter doesn't present enough of a load to pull the voltage down.
I prefer using a solenoid tester unless I need to know the exact voltage, in which case use LoZ or a load should be present.
It is a bit confusing, because normally a digital multimeter will have a high Z input and should show the phantom voltage.
You should think of this as a circuit with extreme voltage drop under load.
In general the issue is that there is some high impedance source of voltage, such as capacitive coupling across the wire insulation or leakage across a switch.
When you measure this with a high impedance meter the voltage is present but if you use a low impedance meter the load of the meter itself is enough to crash the voltage to near zero.
Jon
I just wasn’t sure why my DMM can’t read ghost voltage
Oh, ok.
Use another meter with amp function to check the resistance of the MM 300
Put the DM 300 probes on the voltage, then use another meter to measure the amps going THROUGH THE METER.
From there calculate the resistance..
You could find a voltage in just about anything, even the ends of your toothbrush with a sensitive enough voltmeter.
Sent from my BE2028 using Tapatalk