Open Neutral
- Inside the Beltway
- Engineer
My client friend asked me about a phantom trip issue.
This is the house with PSE's new 100KVA transformer, a 600A fused main, and four 200A panels. Three of them are adjacent to the main, the last has a 200A disconnect there, and the panel itself is in the Mechanical Room at the other end of the house. All panels are new (well, when the job started a few years ago...) SquareD including the fused main.
A few days ago, the MR's panel main and the upstairs disconnect feeding it both tripped. No branch breaker was tripped. There was no unusual work going on that might instigate a trip.
The other three panels have some ilk of surge protectors (Imagery coming), this one does not. But in my thinking all four panels are obviously in parallel, and the three surge suppressors are, too.
The GC called the EC, and there it gets more interesting. They reported that they had recently seen similar anomalies on other SqD panels, and had one case where a shop vac started on another site would trip the SqD main but not a branch. This was repeatable. They've started using C-H panels instead.
I'm at a loss to explain this double-trip. The vacuum cleaner story makes me think "arc-fault grief" but these were {sub}main breakers, not branches.
Is it worth talking to SqD given a lack of data?