i have 120 volts at the fixture with the switch on and 86 with the switch off...is this phantom voltage?...
If you measured with a DMM, it sure is.NolaTigaBait said:i have 120 volts at the fixture with the switch on and 86 with the switch off...is this phantom voltage?...
Measuring voltage across a load accomplishes the same thing. Even a 7-watt night-light bulb works.NolaTigaBait said:thanks, i'll look into a low-impedence meter
Thanks for that link. Know I know how to deal with those voltages that used to boggle my mind.iwire said:
LarryFine said:Mr. Bait, two things:
If you're measuring voltage across the fixture with the bulb in place, somethin is wrong. The load should be enough to eliminate phantom voltage.
Many starters have some switching in the 'neutral' side of the control circuit.mull982 said:Why is this? I've had a similar problem before with a starter coil?
quogueelectric said:I dont believe in ghost voltage. Every voltage is there for a reason and if you cant figure it out keep learning until you can figure it out. Voltage can be a complicated study.