psk101
New member
- Location
- New York, New York
I have two light and power transformers TR1 & TR2. TR1 is 33kV/208V and TR2 is 13.8kV/208V, but their high voltage source is different source generation. TR1 is a delta-wye 33kV/208V. The 33kV supplied to this transformer is from another delta-wye transformer 138/33kV transformer.
TR2 is a delta wye transformer also 13.8kV/208V. but the 13.8kV of this transformer is supplied from a tertiary of an autotransformer (345/138/13.8). The autotransformer is wye-wye-delta configuration. The tertiary is delta winding. Note the generation source for this autotransformer is different than the for above TR1.
Both of these Light and power transformer are connected to a common ATS(automatic throwover switch) and then feed the load. One source is normal while other is emergency.
When I measure the voltage and phase angle across the ATS, the phase angle difference is very large and the voltage readings are not in line.
Ideal reading would be A-A approx 1-2 Volts, but I read 100volts with large phase angle difference. Why would that be? is it because of the high side transformer configurations?
Is it because there are 2 delta-wye conversion (138/33kV & 33/208V) through TR1, but wye-wye-delta to delta-wye conversion (345/138/13.8 & 13.8/208V) through TR2 causing this issue?
TR2 is a delta wye transformer also 13.8kV/208V. but the 13.8kV of this transformer is supplied from a tertiary of an autotransformer (345/138/13.8). The autotransformer is wye-wye-delta configuration. The tertiary is delta winding. Note the generation source for this autotransformer is different than the for above TR1.
Both of these Light and power transformer are connected to a common ATS(automatic throwover switch) and then feed the load. One source is normal while other is emergency.
When I measure the voltage and phase angle across the ATS, the phase angle difference is very large and the voltage readings are not in line.
Ideal reading would be A-A approx 1-2 Volts, but I read 100volts with large phase angle difference. Why would that be? is it because of the high side transformer configurations?
Is it because there are 2 delta-wye conversion (138/33kV & 33/208V) through TR1, but wye-wye-delta to delta-wye conversion (345/138/13.8 & 13.8/208V) through TR2 causing this issue?