The circuit is supplying a fixed piece of equipment to be wired 208 Delta with a 10.5 amp load, supplied by a 120/240 single phase panel.
The customer had already bought a 240 in 240 out rotary phase converter with 48 single phase FLA, and an autotransformer to buck the 240 to 208 before running through the phase converter, and it is rated for 3.68 kVA, 17.71 A, with a max breaker size of 20 A.
I already know that the autotransformer will need to be upsized to handle the phase converter inrush. After speaking with the manufacturer (RONK), they recommended that since the load is only 10.5 A to buy an autotransformer with at least a recommended 40 A breaker size to handle what the phase converter will be using from the line side.
I gathered that the line conductors to the phase converter and the ocpd are to be sized 125% of single phase fla on nameplate, which would be 60 A. According to code, should not that auto transformer be sized for me to put a 60 A breaker in the panel? And if somehow it is okay to put a 40 A OCPD, should my disconnect then be 40 A also because what's the point of a 60 A at that point?And also because 455.6(A)(2) is so confusing the way it's written, are my load side conductors coming out of the phase converter to be the same size as my line conductors? Or can I downsize them based on the load it's serving? Also 455.22 states that I will also need a magnetic motor starter, considering the load, can I put that on the load side of the phase converter with a 20 A overload?
Another side note, I want to tell the customer to take the equipment back and buy a 240 to 208 phase converter for simplicity but he's looking at a four month lead time and is trying to get this piece of equipment up and running ASAP. How can I potentially cut that lead time down?
Thank you for your time.
The customer had already bought a 240 in 240 out rotary phase converter with 48 single phase FLA, and an autotransformer to buck the 240 to 208 before running through the phase converter, and it is rated for 3.68 kVA, 17.71 A, with a max breaker size of 20 A.
I already know that the autotransformer will need to be upsized to handle the phase converter inrush. After speaking with the manufacturer (RONK), they recommended that since the load is only 10.5 A to buy an autotransformer with at least a recommended 40 A breaker size to handle what the phase converter will be using from the line side.
I gathered that the line conductors to the phase converter and the ocpd are to be sized 125% of single phase fla on nameplate, which would be 60 A. According to code, should not that auto transformer be sized for me to put a 60 A breaker in the panel? And if somehow it is okay to put a 40 A OCPD, should my disconnect then be 40 A also because what's the point of a 60 A at that point?And also because 455.6(A)(2) is so confusing the way it's written, are my load side conductors coming out of the phase converter to be the same size as my line conductors? Or can I downsize them based on the load it's serving? Also 455.22 states that I will also need a magnetic motor starter, considering the load, can I put that on the load side of the phase converter with a 20 A overload?
Another side note, I want to tell the customer to take the equipment back and buy a 240 to 208 phase converter for simplicity but he's looking at a four month lead time and is trying to get this piece of equipment up and running ASAP. How can I potentially cut that lead time down?