Please see the attached for the reference.
So we observed Phase current Imbalance in our 13.8KV Main Incoming CBs when our Tiebreaker is closed condition. The maximum difference we observed between IA and IC is 36.9A. But when we Open out Tiebreaker, all three phases become balance.
As our Incoming CBs has 2000:5 CTs and no neutral or ground CTs installed? So what settings are acceptable for the 50G/50N on these Main Incomers?
And why there is no imbalance in the currents when the Tie breaker is OFF? These Main incomers are fed from a Utility substation using a 4000ft Power cable.
So we observed Phase current Imbalance in our 13.8KV Main Incoming CBs when our Tiebreaker is closed condition. The maximum difference we observed between IA and IC is 36.9A. But when we Open out Tiebreaker, all three phases become balance.
As our Incoming CBs has 2000:5 CTs and no neutral or ground CTs installed? So what settings are acceptable for the 50G/50N on these Main Incomers?
And why there is no imbalance in the currents when the Tie breaker is OFF? These Main incomers are fed from a Utility substation using a 4000ft Power cable.