My inverter has a limit of 300 Arms and I am designing the phase connectors to the motor. Does 300 Arms mean that each phase sees 300/sqrt(3) Amps for me top design around?
Thanks!
What exactly do you mean by 'phase connectors'?
If you mean the
three conductors between the inverter and the motor junction box, then as
@JoeStillman says, those conductors will carry up to 300A _each_.
If you are talking about internal connections between the supply terminals and the motor windings, then you _might_ see a 1/sqrt(3) term, depending upon the particular motor connection. For example if the motor is internally delta connected then the current through a delta leg of the motor is 1/sqrt(3) the line current feeding the motor.
Usually an installer isn't worrying about the internal connections of the motor, but the phrasing of your question makes me want to clarify this point.
-Jonathan