Ryan I used the handbook CD-ROM and searched for Balance, Balanced, and imbalance.

There was "hits" on all of these but I do not think they are what you are looking for.

Bob
 

ryan_618

Senior Member
Re: Phase imbalance

I'm doing a plan review and on the panel schedules (120/240V 3Wire 1phase) phase A shows 56 amps and phase B shows 156 amps!!! I can't think that this is permitted, but I sure can't find a reference that backs me up. Help? :(
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Phase imbalance

Ryan here are the spots the words I serched for came up in, I will be glad to search more if you have some other keywords to look for.

Imbalance only came up in the handbook commentary in reference to 445.12, as far as Code these are the articles balance or balanced came up in.

80.15(B), 310.4, 517.2, 520.53, 550.18, 551.42, 552.47, and Annex D
 

bennie

Esteemed Member
Re: Phase imbalance

This is not a phase imbalance. It is a load distribution imbalance on a single phase transformer.

Why is there so much 120 volt load on the one leg to neutral?
 

ryan_618

Senior Member
Re: Phase imbalance

Bennie: I wish I could answer your question. This is not for my city. Once in a while different cities will have me help them with electrical plan reviews/inspections. In all honesty, I don't know much more about the installation than you. They just faxed me some blurry panel schedules and a one-line diagram. I am going to ask for a full set of drawings on Monday.

BTW: Thanks for the terminology correction! :)

Bob: Thanks for your help. I'll start cracking the book. :)

[ October 03, 2003, 07:04 PM: Message edited by: ryan_618 ]
 

ron

Senior Member
Re: Phase imbalance

Depending on how the loads were computed, maybe this one will help.

210.11 Branch Circuits Required
(B) Load Evenly Proportioned Among Branch Circuits. Where the load is computed on a volt-amperes/square meter or square foot basis, the wiring system up to and including the branch-circuit panelboard(s) shall be provided to serve not less than the calculated load. This load shall be evenly proportioned among multioutlet branch circuits within the panelboard(s).
 

brian john

Senior Member
Location
Leesburg, VA
Re: Phase imbalance

This is not a good practise and may cause a voltage imbalance, but if the overcurrent protection and conductors can handle it, whats the problem. (Unless someone can find a NEC violation)
 

bennie

Esteemed Member
Re: Phase imbalance

Effects of a large imbalance;
The transformer winding will develop a major difference in temperature. The core will expand and contract unevenly. Layer to layer faults (shorted turns) are more likely to occur.
 

golfking

Member
Re: Phase imbalance

Originally posted by ryan_618:
Can someone please help me find the code article that addresses phase balancing for feeders?
More information about balancing is in article 220.22
 

charlie

Senior Member
Location
Indianapolis
Re: Phase imbalance

Ryan, I am betting the serving electric utility has something in their service manual. We require the load to be as evenly balanced as possible in order to get (and keep) service from us. Bennie did a good job of listing the reasons for our rule. We will not even permit larger than a 100 ampere single phase commercial service from a 208Y/120 volt transformer because of unbalancing the transformer. :D
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Phase imbalance

Along with what Charlie has said most of the jobs we do have a specification that places the burden on us (the EC) to make sure the initial load balance is with in a certain percentage.

Here is the spec for the job I am on now.
The various circuits served from the panelboards vary in loading. The contractor shall carefully balance the load on each leg of the service. When all load is turned on and the system is operating at 100% the initial unbalance shall not exceed 10%

Note: With 3 phase delta, phases A and C shall be balanced within 10% phase B shall be balanced as closely as possible.
You can see this is a general specification as this job has no 3 phase delta.

Dave or Bennie I have never heard of balance related to volts, always amps, can you give some more info?

As the EC I have some influence on the balance of the amp load, but no influence on the voltage.

[ October 04, 2003, 12:24 PM: Message edited by: iwire ]
 

bennie

Esteemed Member
Re: Phase imbalance

Iwire: It's like the old cliche "what comes first, the chicken or the egg". Load affects the voltage balance. Voltage balance affects the load.

Voltage in a transformer winding attempts to reach an equilibrium. A low current winding will have an elevated voltage that will supply the zero sequence current to the transformer. This current is in the form of circulating current producing unwanted heat.

These are my own words, Dereck, both Charlie's, and many others can express this much better than I can. I only need 8 more years to become an engine ear.
 
G

Guest

Guest
Re: Phase imbalance

<snip>I only need 8 more years to become an engine ear. [/QB]
Is that under the Great-Grandfathered clause? :)

[ October 04, 2003, 11:15 AM: Message edited by: awwt ]
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Phase imbalance

I got you Bennie but the voltage at my service may not be equal before I add any load (transformer may serve other services)

Are you saying I should move my loads around until I get equal voltage on each phase?

It seems like a no win situation anyway as the load is always changing, the way the spec I put up reads it looks to me like they want me to balance the load and let the utility worry about the volts.
 

charlie

Senior Member
Location
Indianapolis
Re: Phase imbalance

The way the spec I put up reads it looks to me like they want me to balance the load and let the utility worry about the volts.
Bob, that is exactly what they and the electric utilities want you to do.

Bennie, whenever a person is in a field as long as we have been, we can be as sharp as an engineer in that narrowly defined part of engineering. In other words, I consider you to be an engineer in your field of endeavor. I am an engineer in power electric distribution. I can not go to another area and be worth a d - - -, I have to stay put. Real electrical engineers have the ability to move around and pick up very quickly.

The bottom line is that I really respect your knowledge and experience even if I don't agree with you all the time. :D
 

bennie

Esteemed Member
Re: Phase imbalance

Charlie, coming from you this is a meaningful compliment. I will work on the areas where you don't agree ;)

I have been fortunate to have been associated with some of the top scientists and electrical engineers in the world. They were from Australia, New Zealand, the UK, Japan, and Russia. I usually hired out by request from the National Science Foundation. I had a good record for performance and received some commendations. I have one signed by Alexander Haig, and one by the Prime Minister of Japan, Mr.Ito
 