Can someone please help me find the code article that addresses phase balancing for feeders?
More information about balancing is in article 220.22Originally posted by ryan_618:
You can see this is a general specification as this job has no 3 phase delta.The various circuits served from the panelboards vary in loading. The contractor shall carefully balance the load on each leg of the service. When all load is turned on and the system is operating at 100% the initial unbalance shall not exceed 10%
Note: With 3 phase delta, phases A and C shall be balanced within 10% phase B shall be balanced as closely as possible.
Is that under the Great-Grandfathered clause?<snip>I only need 8 more years to become an engine ear. [/QB]
Bob, that is exactly what they and the electric utilities want you to do.The way the spec I put up reads it looks to me like they want me to balance the load and let the utility worry about the volts.