One of our hvac techs was sent to a facility to check a Carrier RTU that was not working. This was installed about a year ago with no problems until a storm came through and the unit stopped working. He found the phase loss monitor was not working, He had 240 volts between A-B, B-C, A-C, all were within 1 volt. No neutral, measured 240 volts to ground on two legs but 0 volts to ground on third. Facility electrician confirmed readings and said it was a corner grounded delta system. A replacement PLM was installed but it would not close either. When monitor was bypassed the unit ran fine with all readings normal.
I do not know the make or model number of the PLM but could someone confirm that it should work with this Delta system. Do they typically monitor to ground?
Thanks, Glenn