Re: phase marking
This question come up frequently. In the mid-seventies the NEC did contain a color code requirement. There have been numberous proposals made to have a color code requirement, but the code making panel comment has been " we don't want you to assume the system voltage from the wire color, we want you to test it and be sure"
Who can be sure the correct color will be used in the future. However if you do adopt a color code standard, you may need to post the colors used:
210.4 Multiwire Branch Circuits.
(D) Identification of Ungrounded Conductors. Where more than one nominal voltage system exists in a building, each ungrounded conductor of a multiwire branch circuit, where accessible, shall be identified by phase and system. This means of identification shall be permitted to be by separate color coding, marking tape, tagging, or other approved means and shall be permanently posted at each branch-circuit panelboard.
I suspect this requirement is not often followed.