hugbobandcarol2
Member
- Location
- Broomfield, CO USA
Contractor installed "single phase" 208V receptacles inconsistently resulting in the intelligent rack-mounted power distribution units (PDUs) in falsly indicate power input -- 120V single phase rather than 208-240V.
On the particular receptacles connecting their L1-L2 pins to the "A" and "C" phases the contractor sometimes installed L1 to "A" instead of "C" and L2 to "C" instead of "A". Resulting in: A-B; B-C and A-C rather than A-B; B-C and C-A (or L1-L2; L2-L3 and L1-L3 instead of L1-L2; L2-L3 and L3-L1).
Thus one indicator light is on rather than two. This also causes the intelligent web-based power calculations (and thus capacty limit status) to be wrong.
The contractor is refusing to correct the miswiring stating that it should not make any difference.
Is there a standard indicating that the wiring should be A-B; B-C and C-A (or L1-L2; L2-L3 and L3-L1)?
On the particular receptacles connecting their L1-L2 pins to the "A" and "C" phases the contractor sometimes installed L1 to "A" instead of "C" and L2 to "C" instead of "A". Resulting in: A-B; B-C and A-C rather than A-B; B-C and C-A (or L1-L2; L2-L3 and L1-L3 instead of L1-L2; L2-L3 and L3-L1).
Thus one indicator light is on rather than two. This also causes the intelligent web-based power calculations (and thus capacty limit status) to be wrong.
The contractor is refusing to correct the miswiring stating that it should not make any difference.
Is there a standard indicating that the wiring should be A-B; B-C and C-A (or L1-L2; L2-L3 and L3-L1)?