You sure about that? I thought it was designed for undervoltage protection only? Thought it was specifically an undervoltage relay designed to lock out under single phasing (lost phase)
Well, first, pay attentin to my disclaimer.
Past that, here is what I recall:
[h=6]ANSI 47 ? Negative sequence overvoltage[/h]Protection against phase unbalance resulting from phase inversion, unbalanced supply or distant fault, detected by the measurement of negative sequence voltage.
The one I looked at performed the following calculation:
Vns = 1/3 x (Va + aVb + (a^2)Vc)
where:
Vns is the negative sequence voltage
Va, Vb, Vc are the three phase voltage vectors
"a" is a 120deg phase shift operator
"a^2" is a 240deg phase shift operator
And an Ansi 46 looks at the current
[h=6]ANSI 46 ? Negative sequence / unbalance[/h]Protection against phase unbalance, detected by the measurement of negative sequence current:
- Sensitive protection to detect 2-phase faults at the ends of long lines
- Protection of equipment against temperature build-up, caused by an unbalanced power supply, phase inversion or loss of phase, and against phase current unbalance
And I'm pretty sure you already know all this.
ice