Originally posted by Ed MacLaren:
Although the current and voltage is "out of phase" in any system that has inductive loads(motors, fluorescent lighting, etc.), the term "phase shift" would not normally be used at all by anyone in the electrical wiring industry.
It is more of an electronics term.
We would refer to such loads as having a "power factor" of less than unity (100%).
What are the effects of low power factor on building wiring systems?
The load devices that have low power factor, generally motors, draw more current to deliver the same horsepower than they would if the power factor was corrected.
This causes increased voltage drop and line losses in services, feeders, and branch circuits.
I think the originating poster's question may have been referring to a homework assignment or exam question.
Ed