Gents,
We went to an oil and gas site recently and were asked to evaluate their distribution network. They had blown up a couple of 1000 KVA vfd and each time had been reported that the vfd internals saw 1000+ volts. No mention of where, but on some recording the vfd engineer said he saw that voltage. I never saw the report or anything, but that's what I was told.
The incoming power comes through a 1000 KVA step down from 12470 to 480 through a Wye-Wye xfmr. This splits between a wall of pump controls, mostly small vfd and a large 24 pulse phase shift transformer. The 24 pulse xfmr feeds a 1000 KVA vfd that feeds an 800 hp pump injecting salt water.
Our techs had ran a DGA on the 24 pulse xfmr and found some gassing that pointed towards heating. When we discussed the findings with the site boss he mentioned that a few years ago the 24 pulse xfmr was hot enough they said it glowed at night. On the nameplate of the 24 pulse xfmr it says unbalanced voltages will cause excessive heating of the transformer. When prodding further they said they used to run all the smaller pumps at 70 hz and the larger pump at 63 or more hz but the smaller pumps kept dropping out and faulting with a missing phase fault. So, we figured that excessive loading had cause the phases to become imbalanced which caused excessive heating of the 24 pulse xfmr. So, my first question is that I recognize this can happen, but why does the imbalance cause excessive heating? And can you calculate roughly how much of a temperature increase it can cause, in other words, if I have a 5% voltage imbalance my temp will increase xx%?
Second, when assessing the site I put an amp clamp around one of the grounds on the transformer and it showed 11 amps. While walking the site I put it on every ground I could find and most were between 5 and 10 amps, up to 14 amps. While looking the main step down xfmr I noticed the Xo wasn't ran to the actual ground it just had a copper bonding strap that was about 3" wide and very thin running to the xfmr case right behind the bushing to a nut that was painted. At my previous job commissioning 1 Mw gensets if we didn't use an NGR on the site we had to take neutral to ground with same same ampacity as the phases. Is it not like this on power xfmr? In discussions with a EE it's kind of thought that the site has a weak or open neutral and that if we take the Xo bushing to ground it should alleviate some problems. Any thoughts on this going forward? Other thoughts what might cause the issue with the ground current?
Thanks
We went to an oil and gas site recently and were asked to evaluate their distribution network. They had blown up a couple of 1000 KVA vfd and each time had been reported that the vfd internals saw 1000+ volts. No mention of where, but on some recording the vfd engineer said he saw that voltage. I never saw the report or anything, but that's what I was told.
The incoming power comes through a 1000 KVA step down from 12470 to 480 through a Wye-Wye xfmr. This splits between a wall of pump controls, mostly small vfd and a large 24 pulse phase shift transformer. The 24 pulse xfmr feeds a 1000 KVA vfd that feeds an 800 hp pump injecting salt water.
Our techs had ran a DGA on the 24 pulse xfmr and found some gassing that pointed towards heating. When we discussed the findings with the site boss he mentioned that a few years ago the 24 pulse xfmr was hot enough they said it glowed at night. On the nameplate of the 24 pulse xfmr it says unbalanced voltages will cause excessive heating of the transformer. When prodding further they said they used to run all the smaller pumps at 70 hz and the larger pump at 63 or more hz but the smaller pumps kept dropping out and faulting with a missing phase fault. So, we figured that excessive loading had cause the phases to become imbalanced which caused excessive heating of the 24 pulse xfmr. So, my first question is that I recognize this can happen, but why does the imbalance cause excessive heating? And can you calculate roughly how much of a temperature increase it can cause, in other words, if I have a 5% voltage imbalance my temp will increase xx%?
Second, when assessing the site I put an amp clamp around one of the grounds on the transformer and it showed 11 amps. While walking the site I put it on every ground I could find and most were between 5 and 10 amps, up to 14 amps. While looking the main step down xfmr I noticed the Xo wasn't ran to the actual ground it just had a copper bonding strap that was about 3" wide and very thin running to the xfmr case right behind the bushing to a nut that was painted. At my previous job commissioning 1 Mw gensets if we didn't use an NGR on the site we had to take neutral to ground with same same ampacity as the phases. Is it not like this on power xfmr? In discussions with a EE it's kind of thought that the site has a weak or open neutral and that if we take the Xo bushing to ground it should alleviate some problems. Any thoughts on this going forward? Other thoughts what might cause the issue with the ground current?
Thanks