D!NNy
Senior Member
- Location
- San Luis Obispo
Currently I am doing a coordination study for Phase-Ground Fault curves for my clients recloser and Utility Recloser.....trying to maintain the 0.2Sec of CTI Clearing Time Internval between TCC at any given point of time.
Maximum symmetrical SC data for the phase to ground fault provided by the utility is 4kA @ 12kV on a 3 wire system. Please correct me if am wrong with the following analysis.
I am not able to maintain 0.2sec CTI at the maximum short circuit current. As the utility and client reclosers are at the same location there is no difference between the SC current.
My argument is in a 3 wire system when will possibly have the maximum SC current 4kA for phase to ground fault with out having the 4th wire. Maximum available SC current listed by the simulating software is as if there is short circuit current between the source and single phase conductor along the ground (perfect ground of zero resistance ) or 4th wire.
If i am correct why the utility is providing the single phase to ground fault current 4kA, In reality this may be very low as there is no zero resistance ground return path to the source or 4 th wire.
Thanks in advance for the suggestions.
Maximum symmetrical SC data for the phase to ground fault provided by the utility is 4kA @ 12kV on a 3 wire system. Please correct me if am wrong with the following analysis.
I am not able to maintain 0.2sec CTI at the maximum short circuit current. As the utility and client reclosers are at the same location there is no difference between the SC current.
My argument is in a 3 wire system when will possibly have the maximum SC current 4kA for phase to ground fault with out having the 4th wire. Maximum available SC current listed by the simulating software is as if there is short circuit current between the source and single phase conductor along the ground (perfect ground of zero resistance ) or 4th wire.
If i am correct why the utility is providing the single phase to ground fault current 4kA, In reality this may be very low as there is no zero resistance ground return path to the source or 4 th wire.
Thanks in advance for the suggestions.