What is phase to phase and phase to ground fault current for 1500kva transformer 5.75% impedance 480/277V three phase system?
To get the real secondary fault current, you really need to know the available fault current on the primary.
You can do a worst case "infinite bus" calculation for the secondary fault current.
First find the secondary full load current 1500000/480/√3 = 1804 amps
Divide that by the percentage impedance in decimal form
1804/.0575 = 31,374 amps available fault current at the secondary terminals of the transformer, but in the real world, the actual fault current will be less, because the primary current is limited, not infinite.
I don't remember and am not going to look it up.
There are online calculators and Bussmann has a free app called FC².
Why the interest? These values are typically lower than the three phase symmetrical fault current value.That app only tells three phase currents not phase to ground fault current
Why the interest? These values are typically lower than the three phase symmetrical fault current value.
After secondary conductor lengths of 50' or so the L-L will exceed the L-G.Not in some cases. Therefore the interest
Sent from my iPhone using Tapatalk
It appears you know how to use the internet, so do a search.That app only tells three phase currents not phase to ground fault current
Excerpt from IEEE Violet Book, Chapter 2. (Diagrams omitted)Not in some cases. Therefore the interest
The fault current calculator on Mike Holt's main site under free stuff will calculate this - it will be assuming infinite line side capacity, just enter the transformer size, impedance and secondary voltage.What is phase to phase and phase to ground fault current for 1500kva transformer 5.75% impedance 480/277V three phase system?
Is that 115% as in 2 / sqrt(3)? I.e. the imepedance of the L-G fault at the transformer will be 1/2 as much (half as many transformer coils are involved) but the L-G voltage is 1/sqrt(3) times the L-L voltage?Assuming this is a delta-wye transformer, a line to ground fault at the transformer will have fault current that is about 115% of the calculated three-phase bolted fault current at the transformer.
Is the IEEE document not stating it can be ignored?Assuming this is a delta-wye transformer, a line to ground fault at the transformer will have fault current that is about 115% of the calculated three-phase bolted fault current at the transformer. However, as noted, the fault current will decrease pretty quickly as the distance to the fault increases.
For a wye-wye transformer (commonly used by utilities), it will be less than this - you need to know the utility zero sequence impedance.