Hi all, been reading the forum for a while but this is my first time posting. Thanks for all the information.
I am trying to make sense of some fault current waveforms from a fault just outside a transformer. By all appearances, this is a single-phase to ground fault. To confirm, I calculated the symmetrical components of the fault waveform (I can't upload pictures yet as I am a new user).
It is my understanding that a single-phase to ground fault should produce equal magnitude I0, I1, and I2, all in phase, because the fault puts the sequence networks in series. However, I am seeing equal magnitude I1 and I2, but a zero-sequence current I0 with roughly half the magnitude of I1 and I2. All are roughly in phase.
Does anyone have any insight into what this might tell me about the fault? I haven't seen a similar fault signature in any textbooks or online examples. My instinct is either this means it is not a "pure" phase-to-ground fault (i.e., there is some involvement from another phase), or it has something to do with the fact that these fault traces were taken at a slight distance through the line impedance, not directly at the fault itself.
Any insight is much appreciated.
I am trying to make sense of some fault current waveforms from a fault just outside a transformer. By all appearances, this is a single-phase to ground fault. To confirm, I calculated the symmetrical components of the fault waveform (I can't upload pictures yet as I am a new user).
It is my understanding that a single-phase to ground fault should produce equal magnitude I0, I1, and I2, all in phase, because the fault puts the sequence networks in series. However, I am seeing equal magnitude I1 and I2, but a zero-sequence current I0 with roughly half the magnitude of I1 and I2. All are roughly in phase.
Does anyone have any insight into what this might tell me about the fault? I haven't seen a similar fault signature in any textbooks or online examples. My instinct is either this means it is not a "pure" phase-to-ground fault (i.e., there is some involvement from another phase), or it has something to do with the fact that these fault traces were taken at a slight distance through the line impedance, not directly at the fault itself.
Any insight is much appreciated.