Is the amount of fault current that can flow phase to phase different than phase to ground in a simple infinite bus calculation? Here's how I was doing it. It differs from a number of reputable publications that suggest instead to start with xfmr FLA and then divide by percent impedance. However it gets the same result as what those publications publish:
For a 2000 KVA xfmr with 5.75%Z 277/480Y
*Since the xfmr is a percent short circuited, I find the full short circuit KVA by dividing it by the impedance, then divide that by voltage to get amperage.
(XFMR VA/XFMR%Z)/(V-Phase*3)
(2,000,000/0.0575)/(277*3)
41856 amps
The same result could be achieved by first dividing total KVA by 3 (amount of KVA per phase winding) then dividing that by the percent impedance, then dividing that by the line voltage.
((XFMR VA/3)/XFMR%Z))/(V-Phase*3)
((2,000,000/3)/0.0575))/277
If the fault were phase to phase, would it be to multiply total KVA by 2/3 (KW for 2 phases) and then divide that by percent impedance then divide that by line to line voltage? It seems that way to me at the moment but if I tried to consider the L-G and L-l shorts instead as just resistive circuits in a 3 phase system, then it doesn't seem this way. We know I line and I phase are the same for a 3 phase load but when trying to think of a source short circuit scenario I am getting confused a bit. Would this be a L-L short circuit calculation:
(XFMR VA*(2/3))/XFMR%Z/(V L-L)
2000000*(2/3)/0.0575/480
48309 amps
For a 2000 KVA xfmr with 5.75%Z 277/480Y
*Since the xfmr is a percent short circuited, I find the full short circuit KVA by dividing it by the impedance, then divide that by voltage to get amperage.
(XFMR VA/XFMR%Z)/(V-Phase*3)
(2,000,000/0.0575)/(277*3)
41856 amps
The same result could be achieved by first dividing total KVA by 3 (amount of KVA per phase winding) then dividing that by the percent impedance, then dividing that by the line voltage.
((XFMR VA/3)/XFMR%Z))/(V-Phase*3)
((2,000,000/3)/0.0575))/277
If the fault were phase to phase, would it be to multiply total KVA by 2/3 (KW for 2 phases) and then divide that by percent impedance then divide that by line to line voltage? It seems that way to me at the moment but if I tried to consider the L-G and L-l shorts instead as just resistive circuits in a 3 phase system, then it doesn't seem this way. We know I line and I phase are the same for a 3 phase load but when trying to think of a source short circuit scenario I am getting confused a bit. Would this be a L-L short circuit calculation:
(XFMR VA*(2/3))/XFMR%Z/(V L-L)
2000000*(2/3)/0.0575/480
48309 amps