Phase voltage of 120/208 3 phase?
mta145
In the NEC exam preperation book on page 8 the square root example no. 2 states that the phase voltage of 120/208v is 208 divided by 1.732 which equals 120v. Can someone explain how the phase voltage of 120/240v equals 120 and not 138?
ron
Because 120/240 is not three phase.
A 240V residential style feeder is essentially 240V line to line with the 120V line to neutral voltage being a tap in the middle of the single transformer coil.
infinity
New Jersey
Journeyman Electrician
Think of it this way, you walk west 120' from a given starting point (X), now you go back and walk east from that same starting point. How far apart are the two end points?
120'.........................X..........................120'
0.........................................................240'
For a WYE system you would walk 120' and then walk on an angle 120 degrees away from the first line the resultant distance that you've walked in 208' (120' * 1.73)
mta145
what is the phase voltage of 120/240 3phase?
high leg
high leg
120/240 3 phase is a high leg system. 120 A to neutral. 120 C to neutral.
208 B to neutral, B being the high leg (orange color coded)
240 A to B; 240 B to C ; 240 A to C
realolman
The squigglies are the three transformers... sorry about the crappy picture.
I also believe the 180 is not correct... I wanted to edit this before the 10 min deadline. SHould be 208 or .866 times any of the phases
realolman
Well I missed the deadline, so now my stupidity lives in cyber eternity... perhaps beyond the time I can keep it going during my lifetime.
Here's the edited drawing:
Hi leg = .866 x 240
That's probably one of the best ways I have seen vector math explained.
Good job.