No Larry. I am describing three secondaries from three transformers on three separate poles.
That's not a 3-ph transformer bank; that's three individual 1-ph transformers feeding separate services, and not germain.
The primaries are typically connected in a wye, and the three center-tapped 240V secondaries share only a common neutral/ground wire.
Again, you're describing separate 1-ph secondaries. The three neutrals are common because they're all grounded, of course.
Each primary is connected to a different phase. Some of your neighbors receive a single phase service +/- 120 degrees out from your own.
No disagreement there, but that has nothing to do with this sub-discussion, which is comparing the center-tapped secondary of a high-leg Delta to that of a 1-ph service.
My point is that these secondaries cannot be connected in a delta as they are in a high leg service.
Well,
one of them can, which leads to the point (okay,
my point):
If you put all three of those transformers with the 120/240v secondaries onto a single pole, connect them in a Delta, and only ground ONE center tap, you have a high-leg Delta.
And, if you compare that one, center-tapped-and-grounded secondary to the secondary of one of your individual 120/240v 1-ph transformers, you will see absolutely no difference.
There's 240v between the two ends, and 120v between each end and the neutral. As Mr. Trotter said in My Cousin Vinny, "I-dentical!"