My take on "close proximity" is the standard design drawings shown in the NEC for duct banks, typically 7.5" on centers.
Even if you are using PVC conduit, there is no reason not to install A-B-C-N-G in each conduit so that the net magnetic flux from those cables is minimized.
If you insist on using non-magnetic conduit and running A-A-A all in the same conduit, etc. then you will need to perform finite element modeling to determine the net magnetic fields and the amount of current induced in rebar.
There are plenty of horror stories about people using RGS conduit and installing one phase in each conduit, the conduit heats up and melts the wire.
When a transformer manufacturer installs a bushing in a transformer tank, they typically install a stainless steel panel for the bushings to penetrate to avoid the magnetic effects on the steel tank.