A Alwayslearningelec Senior Member Location NJ Occupation Estimator Dec 22, 2021 #1 These values listed on each phase( A,B,C- 1.86 each) would be the draw/current? BTW why does my message have to be at least 100 characters? lol Attachments Capture.JPG 67.3 KB · Views: 20
These values listed on each phase( A,B,C- 1.86 each) would be the draw/current? BTW why does my message have to be at least 100 characters? lol
R Rock86 Senior Member Location new york Occupation Electrical Engineer / Electrician Dec 22, 2021 #2 That's either the current draw, or kW rating for load calculations. My guess would be that it is kW for load balancing on the spreadsheet they are using.
That's either the current draw, or kW rating for load calculations. My guess would be that it is kW for load balancing on the spreadsheet they are using.
M main197 Member Location California Occupation EE Dec 22, 2021 #3 Looks like kVA in each phase. Total 3 phase load=3*1.86kVA=5.58KVA. This is equal to 15.48A at 208V (5.58/(1.732*0.208)).
Looks like kVA in each phase. Total 3 phase load=3*1.86kVA=5.58KVA. This is equal to 15.48A at 208V (5.58/(1.732*0.208)).