I'm working with a local hockey rink and the electrical system is experiencing phase imbalances when large 3-phase motors are running. The chiller and main cooling tower units are both 3-phase and when in operation, B phase becomes 10% out of balance with A, and C becomes 10% out of balance with B.
Any ideas on what could be causing this? There is a large capacitor at 150 KVAR. There is also a VFD feeding a cooling tower.
"Out of balance" kind of implies that two of three phases are the same, are you saying that if A=100, then B=90 and C=80? What about each piece of equipment is operating separately? Actual current and voltage readings, as well as where you're measuring, are usually helpful.
Has the PFC been checked? If some or all the caps on one phase are out, that could mess with what you're measuring.
What is C in reference to A?
System voltagetotalFLA of Motor
% VOLTAGE IMBALANCE
480.00​
6.67%​
% CURRENT IMBALANCE
200.00​
PHASEVOLT w/LoadAmp No PFC Cap
A-B
480.00​
16.00​
100.00​
B-C
432.00​
32.00​
90.00​
A-C
480.00​
MAXMAX-AVG
16.00​
100.00​
MAX
AVG
464.00​
480.00​
16.00​
32.00​
96.67​
100.00​
STAND DEVIATION
22.63​
4.71​
TOTAL IMBALANCE
6.90%​
Investigate
6.90%​
OK, if not SFA