ghelec
The 1800w rating is for resistance loads if you look on the photo cell it should say something like 1800 watt tungsten, 1000 watt ballast.
For a 1000 watt HID fixture if you add the ballast wattage to the lamp wattage you will be over the rating of the photocell. You need a relay type photocell as a thermo type will not take the extra wattage.
An Intermatic 1121 should be effective in solving your problem. It has a 1800 watt rating for both tungsten and ballast.
Edit to add that you cannot use a thermo type photocell if your ballast is connected to 240 volts and the photocell is a 120 volts, If it is a relay type it can be done but you must connect the neutral from the photocell to a supply neutral. the other hot will go straight to the ballast. Not a good design though.