Photovoltaic wiring conduit type

Status
Not open for further replies.

Npstewart

Senior Member
Thanks raider. I had someone call me about a photovoltaic system they are helping a EC with. The EC installed everything in schedule 40. Now apparently the conduits have shrunk out of the fittings leaving exposed wiring. Anyone have experience with this? I was looking at 690.31 (A) under the "FPN" . It talks about high temperatures for installation.

It doesen't surprise me as things tend to shrink when cooled and expand when heated.

Any input would be interesting.
 

c_picard

Senior Member
Location
USA
pvc's OK if listed for the temp,

If you engineer for record hot/cold + ambient adder
you need an expansion fitting after 5' i upstate NY,
extreme bu necesary.
 