When the NEC references protecting conductors from “physical damage”or “physical protection” what exactly does that mean ? Is there a definition in article 100 I can’t seem to find one ? What determines where an area is deemed as requiring physical protection . is there a certain height off the ground ? Thanks


Sent from my iPhone using Tapatalk
 
Pretty much up to the interpretation of the AHJ, the NEC offers no formal definition.
 
I agree - totally an interpretation.

Exposed non metallic covered cable on a wall - may be subject to physical damage if there is any kind of traffic that ordinarily passes by.

Same location but with rigid steel conduit - maybe not considered subject to physical damage by pedestrian traffic, still possibly subject to damage by vehicular traffic, especially something like a Caterpillar D9.
 
There are some places where NM cable and communication cables cannot be run, due to the nature of location. For instance, small gauge non-metallic cable cannot be run perpendicular under floor joists in a basement because people tend to hang things from it, which can pop loose the staples securing it, or in worst-case damage the cable.

On your other similarly related topic, I mentioned the ***.24 sections of the NEC which state that cables installed Exposed on the surface of ceilings and sidewalls shall be supported by the building structure in such a manner that the cable will not be damaged by normal building use. Going in Step farther, I would say would not be damaged by normal occupant use either.

As others have written, there is no defined standard. The way I do it is I try to figure out if there is any way under normal conditions that a cable would be damaged. You could run telephone cable tucked under the cove base in a room, however I would not run it under a carpet knowing that chairs could be rolled across it, a woman with high heels could step on it, etc.

I believe that under Virginia IRC, cables were or are required to be protected below 7 feet. I have done a few installations with a surface mount metal switch box, and a stub running up near the ceiling to protect the NM cable running to it.

Then again, the local cable company has done many installs where they simply lay the cable in the crawlspace and do not attach it to the structure. If I had to guess as to reasoning for that, it's that a lot of coax gets installed with NM Staples and strung like banjo strings, which will eventually cause signal problems.
 
Years ago we did a service upgrade that had PVC on the side of the house. The inspector started asking me how far the conduit was from the alley. I told him over 6 feet. He said that was not subject to physical damage. I had him come to the house and showed him where the conduit had been split by a snow plow.

We did that part in rigid.
 
Years ago we did a service upgrade that had PVC on the side of the house. The inspector started asking me how far the conduit was from the alley. I told him over 6 feet. He said that was not subject to physical damage. I had him come to the house and showed him where the conduit had been split by a snow plow.

We did that part in rigid.
Nobody was concerned about snow plow possibly damaging more then just that conduit??
 